Seeking Guidance on Path Length settings #12086
Replies: 3 comments 8 replies
-
This is not a code issue. Let's transfer this to a Discussion. I will answer there. |
Beta Was this translation helpful? Give feedback.
-
Yes, when there is water vapor and CO2 in the atmosphere, it is good to account for this when looking at radiative flux to a distant target.
This depends on the size of the fire. If you really are in a point source regime, say 1 m flame and 30 m to target, then I would not think you need to change the path length. If the distance to the target is cut in half by the wind and tilt of the flame, then I would factor that in. |
Beta Was this translation helpful? Give feedback.
-
The PATH_LENGTH is characteristic length scale used to compute an effective gray-gas absorption coefficient. It is not the actual distance that is used when calculating the heat flux from A to B. I suggest you do a quick sensitivity analysis to see how much it matters. |
Beta Was this translation helpful? Give feedback.
-
Hi all,
Historically I have been using the following setting for my FDS runs:
&RADI NUMBER_RADIATION_ANGLES=600, PATH_LENGTH=30.0 /
where the path length is equal to the distance between my target and the burner fire.
My question is whether using the distance between the target and the fire base is a valid choice for the path length. I have seen some literature that suggests that this is a decent approximation for far-field targets. My secondary question is whether the path_length should change when wind is introduced. For example, if I add a 5 m/s wind in the direction of the target, the flame will be much closer to the target... should the path length change to account for this reduced distance between the flame and the target.
Thanks!
Beta Was this translation helpful? Give feedback.