The aerodynamic area results from the pressure drop due to flow contracting to enter the vent and expanding after it leaves the vent. If you have sufficient grid resolution you will resolve that flow and the pressure drop will happen naturally. If you are coarsely resolving the opening then you can model it with HVAC where you can specify a duct loss that gives you the equivalent of C_d=0.7 |
Beta Was this translation helpful? Give feedback.
-
Thanks. I suppose I have to specify two hvac vents and connect them with a damper type duct. What should I specify for the length and area of duct, and the forward, reverse loss, and roughness type and value. |
Beta Was this translation helpful? Give feedback.
-
If I know the free area of an openable vent at the head of stair is 1m2. The aerodynamic free area is 0.7m2 as the coefficient of discharge is 0.7. How can I model this realistically for pressure drop. Should I model a 1m2 hole opening, or is there a way to specify coefficient of discharge.
Beta Was this translation helpful? Give feedback.