TRV demand doesn't trigger boiler to switch on #783
-
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 4 replies
-
I've updated the diagram as I realised I hadn't shown the relationship between VTherms and the Central Configuration: |
Beta Was this translation helpful? Give feedback.
-
Hello, Before answering totally and fully read all your post, I don't understand the need of the Second, with Sonoff TRVZB, you should not configure the "closing degree" as explain here: https://github.com/jmcollin78/versatile_thermostat/blob/main/documentation/en/self-regulation.md#self-regulation-by-direct-valve-control If "closing degree" is configured, the hvac_action of the Sonoff TRV don't work and then VTherm can't know that the VTherm need for heat and don't activate the central boiler. You should first those 2 tips before going on further. |
Beta Was this translation helpful? Give feedback.
Yes it is better like this. Controling your central boiler with an
over_switch
is really not a good idea because start and stop are constant.