Hello @adriannow , Can you send us the configuration of your VTherm (see: https://github.com/jmcollin78/versatile_thermostat/blob/main/documentation/en/reference.md#custom-attributes) |
Beta Was this translation helpful? Give feedback.
-
Sure, but from the initial observation, the VTherm is trying to manipulate the valve correctly - it may just be problem with the Sonoff TRVZB itself. Here are my settings:
|
Beta Was this translation helpful? Give feedback.
-
I'm facing the same problem with nearly all of my TRVZBs. I'm in touch with Sonoff to figure out a solution. I had the impression that shifting arround the"max_valve_closing_degree" would make the TRVZB shift gradually from its calibration state. In my case i had to recalibrate the valves nearly every day. I'm currently on 1 min heating cycles and will follow your suggestion and try out 10 minutes cycles to see if it does any good. If that doesn't help my idea would be to use an additonal offset of -1°C on the temperature calibration, and just manipulate the "max_valve_opening_degree" and leave the "max_valve_closing_degree" at 100% . It is not hte most elegant way but maybe worth a try if the 10 min cycle does not solve the problem. |
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
I have noticed this issue with my Sonoff TRVZB this evening. I have a 10% (10) regulation threshold configured and valve closing degree at 100, valve opening degree at 0. Vtherm and trv showing as idle (not heating) but I could hear water flowing through and the radiator was hot. The valve has been installed for 10 days (it was also calibrated 10 days ago) and is on firmware 1.2.1. Setting the valve closing degree to 0 and then back to 100 resolved the issue. |
Beta Was this translation helpful? Give feedback.
-
So, should I still not use |
Beta Was this translation helpful? Give feedback.
-
Hello, I'm testing SONOFF TRVZB thermostatic radiator valve, and I was quite happy regarding precise control of valve opening (using valve opening/closing degree) in Versatile Thermostat. Just so everyone knows, by default Sonoff only opens valve to 0/100%, so it's going through some heavy cycles.
After initial testing everything looked fine, but then I noticed that the radiator is quite warm even after few hours when the valve should be 100% closed. So I've added additional thermometer directly on top of the radiator to see how it looks in reality:
(From the top: blue line is temperature directly on top of the radiator, yellow - set temperature (it was constant 23.5 degrees). And then looking at the second graph of the "Valve open percent", even after about 3 hours the radiator was still significantly hotter than the ambient temperature (measured less than meter away). So in short, valve was definitely not closed fully.
After I reinserted batteries and reset the TRVZB, it seems to recalibrate and close fully again. After about a day the problem started again.
I'll be trying to do some automation maybe to close fully and open the valve fully from time to time, to get the thermostat to recalibrate (as this is what it does after all on default firmware). But at this point I'm not sure if this will help - just my best guess.
Beta Was this translation helpful? Give feedback.