Hey Mate, yeah that's the one C (Common) to 3/2 or 1... From memory DRM-3 limits outdoor unit power consumption to 75% of rated capacity, DRM-2 is a 50% limit and DRM-1 is Compressor off... Pretty sure its 5v logic so can be driven by relay or for testing just bridge it...

Add 0x8236, 0x8237 & 0x8238 as custom messages, these are the frequency variables of the compressor.. Get the unit running at maximum Heat or Cool (Depending where you are) then bridge one.. Within a few seconds those variables will change and also 0x80A7 will give you a number..

There is also 12v on CN303, so you should be able to power an esp32 relay board and let it live inside the outdoor unit.