For the M-Stop wires you can connect those directly to the 24-48V power supply you are using similar to the power wires. One way we do this is just connecting them to the same power splitter as shown in this image below:

If you intend on using an M-Stop Button what you would want to do is put that button in series connection with the blue and yellow wires to the first actuator in your chain and make sure your "M-STOP STRATEGY" on the actuators is properly set to "MOTOR HOLD" (if you want your actuators to hold position when the M-Stop power is cut) or "MOTOR OFF" (if you want the motor to be back-driveable when the M-Stop power is cut).

NOT RECOMMENDED (but also viable): Finally, if you…