Eurotronic CometZ TRVs dont/stop reporting temperature incrementally as configured #6634
Replies: 4 comments 6 replies
-
I think this is a combination of suboptimal connectivity with excessive reporting from energy meters and multisensors. There are stretches in that log where such reports are received every 100 ms for a few seconds straight. In some other instances, they are re-transmitted over and over, essentially flooding the network. Please give this a good read and try to apply it throughout. Z-Wave really isn't a good fit for energy metering, especially when devices report changes of 0.03 W:
or no change at all:
Then we can come back at trying to diagnose the TRV issue. As it stands, the controller drops down to 40 kbps from the get-go although the device supports 100 kbps, which indicates a suboptimal connection to the TRV. And later during the interview, even that stops working reliably, causing several queries to time out. I think the devices are simply having trouble sending the reports to the controller. Lots of power meters "talking" over them doesn't help. FWIW, the update at 9:07 is triggered by Z-Wave JS because it hasn't gotten one in 6 hours:
|
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
Before the weekend I tried to reduce the devices reporting metering where I didn't need it, but saw no difference from the CometZ TRV. I was away for the weekend and made no changes since. At that point I didn't have debug enabled, but I enabled it so some of the working reporting has definitely been captured later on: It remains to be seen if they will continue to behave or revert back to not appearing to report. |
Beta Was this translation helpful? Give feedback.
-
OK, Last night I noticed this again, two TRVs in the same room. One working perfectly still and the other back to the old ways: |
Beta Was this translation helpful? Give feedback.
-
Checklist
I have read and followed the above instructions
I have checked the troubleshooting section and my problem is not described there.
I have read the changelog and my problem was not mentioned there or the fix did not work.
Describe the issue
What is happening?
The multilevel sensor reports are not happening consistently and as configured (0.5 degree) unless manual refresh in JSUI is made. Then they reflect current temperature. A re-interview may solve this for a while, not always, but the issue can re-occur.
What did you expect to happen instead?
configured (default 0.5 degree) reports are reported in Home assistant
Steps to reproduce the behavior:
Anything else we should know?
These TRVs are the 'new version' of the Eurotronic spirit. Similar issues with the spirits were reported here (I have nearly 20 spirits included and they operate perfectly):
https://community.home-assistant.io/t/eurotronic-spirit-z-wave-room-temperature-doesnt-refresh-with-z-wave-js/348981/3
I've seen this behavior on at least 6 CometZ's dispersed in a 60 node (mostly powered and repeater) well meshed network, and the same actions sometimes get them working again.
In the image attached is an example of how they behave with this issue before and after re-interview. You can clearly see the difference
With a manual refresh the temperature can change at least 5 degrees.
For completeness, I already reported some other strange behaviour with these exact devices and noted this problem here --> hassio-addons/addon-zwave-js-ui#620
Relating to the logfile, just after 18:00 - debug enabled
Shortly after nodes 146 and 145 were changed to setpoint 19.5 and the room heated (2 radiators in the same room)
Shortly before 19:10, #146 updated by itself, and Air temp jumped from 12-19 degrees!
Shortly after 19:11 i performed a manual sensor refresh on #145
Around 17:25 - re-interview #145
Around 19:51 - re-interview #146
Around 21:01 manual sensor refresh on #146
(also in network are non-problematic spirits #34,36,149,23,21 etc
Software versions
Driver (node-zwave-js): 12.4.1
Z-Wave JS UI: 9.7.1
Home Assistant (Yellow - but occurred the same on Pi)
Core 2024.1.5
Supervisor 2023.12.1
Operating System 11.4
Frontend 20240104.0
Aeotec Gen5+ controller
Device information
Manufacturer: Eurotronic
Model name: CometZ
Node ID: 146 & 145
Checklist
I made sure to provide a driver log on level debug.
The log includes a re-interview of the problematic device (if applicable).
The log includes the problematic interaction with the device (if applicable).
I provided the node ID of the problematic device (if applicable).
Upload Logfile
zwavejs_2024-01-23.log